Discussion forum about Comet system products
You are not logged in.
I cannot communicate with T3511 using TSensor. Www pages are visible.
Net settings are following:
T3511:
IP: 134.65.210.97
mask: 255.255.255.192
gateway: 134.65.210.65
PC:
IP: 134.65.124.19
mask: 255.255.255.192
gateway: 134.65.124.1
Are above settings OK?
Last edited by Jacek (20-06-2007 13:15:52)
Offline
Settings looks OK. Can you set the T3511 via telnet?
( in Start Windows menu select run and type cmd. Then in command window enter
telnet 134.65.210.97 9999
)
Offline
Yes, it is possible to telnet to this unit.
Last edited by Jacek (21-06-2007 11:00:01)
Offline
I tried to extend communication timeouts in software and I sent this software version by your email. Could you test it, please?
Offline
Unfortunately this version also don't work at all.
It works only in this same subnet. After connecting transmitter to other subnet it is impossible to connect to the sensor using TSensor.
BTW: Which ports should be opened for communication between TSensor and ethernet transmitters?
Last edited by Jacek (22-06-2007 09:43:42)
Offline
TSensor application need open these ports:
TCP: 9999
TCP: 502 for ModBus
UDP: 0x77FE for reading connection settings
It is possible that connection failed on UDP port.
Offline