We use 4 ,P8541 sensors to monitor bearing temperatures. These sensors measure 4 temperatures each.
Strangely enough we recieve from time to time an email with an overflow at channel 6, but we only have 4 channels!
All sensors report this at the same time. See below for a typical email: (what is wrong here?)
Firmware version: 4-4-1.04, Web version: 1.00.
Typical email from sensor with "channel 6 overflow"
Temperature at channel 6 overflow
Channel 1 temperature: 27.6 °C
Channel 2 temperature:28.0 °C
Channel 3 temperature:28.2 °C
Channel 4 temperature:27.9 °C
Alarm settings:
Channel 1:
Upper Limit: 60.0 °C, Lower Limit: 0.0 °C, Hysteresis: 1.0 °C, Alarm Delay: 120 s
Channel 2:
Upper Limit: 60.0 °C, Lower Limit: 0.0 °C, Hysteresis: 1.0 °C, Alarm Delay: 120 s
Channel 3:
Upper Limit: 60.0 °C, Lower Limit: 0.0 °C, Hysteresis: 1.0 °C, Alarm Delay: 120 s
Channel 4:
Upper Limit: 60.0 °C, Lower Limit: 0.0 °C, Hysteresis: 1.0 °C, Alarm Delay: 120 s
For actual info visit http://192.168.2.66 . Have a nice day.
Offline
You have wrong settings of SNTP server. Disable synchronization with SNTP server, or insert the correct SNTP server IP address. The "channel 6 owerflow" is a bug, we repair it in next firmware version.
Offline
Thanks, i have disabeled SNTP for now....