P8541 sensor sending emails with "channel 6 overflow"

We use 4 ,P8541 sensors to monitor bearing temperatures. These sensors measure 4 temperatures each.
Strangely enough we recieve from time to time an email with an overflow at channel 6, but we only have 4 channels!
All sensors report this at the same time. See below for a typical email:   (what is wrong here?)


Firmware version: 4-4-1.04, Web version: 1.00.

Typical email from sensor with "channel 6 overflow"

Temperature at channel 6 overflow

Channel 1 temperature: 27.6 °C

Channel 2 temperature:28.0 °C

Channel 3 temperature:28.2 °C

Channel 4 temperature:27.9 °C

Alarm settings:
Channel 1:
Upper Limit: 60.0 °C, Lower Limit: 0.0 °C, Hysteresis: 1.0 °C, Alarm Delay: 120 s 

Channel 2:
Upper Limit: 60.0 °C, Lower Limit: 0.0 °C, Hysteresis: 1.0 °C, Alarm Delay: 120 s 

Channel 3:
Upper Limit: 60.0 °C, Lower Limit: 0.0 °C, Hysteresis: 1.0 °C, Alarm Delay: 120 s 

Channel 4:
Upper Limit: 60.0 °C, Lower Limit: 0.0 °C, Hysteresis: 1.0 °C, Alarm Delay: 120 s 

For actual info visit http://192.168.2.66 . Have a nice day.

Offline

 

#2 20-07-2007 09:38:56

PavelM
visitor
Registered: 29-05-2007
Posts: 45

Re: P8541 sensor sending emails with "channel 6 overflow"

You have wrong settings of SNTP server. Disable synchronization with SNTP server, or insert the correct SNTP server IP address. The "channel 6 owerflow" is a bug, we repair it in next firmware version.

Offline

 

#3 20-07-2007 14:34:06

keesscherer
Member
From: Vorden, Netherlands
Registered: 19-07-2007
Posts: 2
Website

Re: P8541 sensor sending emails with "channel 6 overflow"

Thanks, i have disabeled SNTP for now....