Iam facing problem with P8541 and need assistance
I have four temperature probes connected with P8541 three are working fine but fourth channel temperature is not working temperature probe is fine and in working because I swapped that probe with other channel and its working the problem is in some setting its shows some sort of clone message and ROM code is 000 all zeros where as other channel ROM address is some number kindly help me in the matte
Offline
Hi,
Sorry, I don't understand your issue. Please send better description of your problem (with screenshots) to support@cometsystem.com.
There is no difference between RCA connector on the device. All connectors are equal. If you physically exchange probes between connectors, channel order will be still same. If probe works in one connector and not working at another, it look to damaged connector in device.
Regards,
Jan
Offline
The P8511 transducer is designed to measure temperature through the single external DS 18B20 sensor. The P8541 transducer is designed to measure temperature through the four external DS 18B20 sensors. Sensors are connected through the cinch connector. The P8510 measures temperature through the internal DS 18B20 sensor. The communication with meter is over Ethernet.