Hi,
we have some problems with modbus connections from the P8511 temperature sensors. We poll the sensors with an interval of 1 second and sometimes we receive over a longer timeperiode (10-20s) the value of 65535 from the sensors. Is this value an error code and what can we do to avoid this situation.
Best Regards
Lars Martin
Offline
Hello Lars,
I haven't heard about this problem before. But I think reading interval is too fast. Device measure temperature with interval 2 sec. Fastest reading not make sense from this reasons:
- reading interval is 2 sec
- response time of useed probe is not faster than ~3 sec
A few hints:
- decrease reading interval to 5 sec (or better 10 sec)
- close TCP connection after every communication (open socket, send command, wait for answer, read answer, close socket)
John