P8511 Modbus read issues

Hi,

I am using P8511 Ethernet temperature sensor and want to read temperature from the modbus register. I tried reading using a Sixnet VersTRAK uIPM RTU as well as from my workstation using Modbus Poll (mbpoll.exe) shareware. Doesnot work in either case. I am getting invalid address error.
I have configured address from 40001 and function i am using is 0x3 (block read) as per the P8511 documentation

Any idea on what could be the problem ?

Thanks,
Rakesh

Offline

 

#2 27-08-2007 07:37:29

PavelM
visitor
Registered: 29-05-2007
Posts: 45

Re: P8511 Modbus read issues

Probably you have wrong settings in your modbus software. We tried read operation with Modbus Poll successfully. Below is image with setting.
http://forum.cometsystem.cz/img/user_img/mbpoll_setup.jpg
You can use our SensorReader software for test. For capturing and debugging ethernet communication I recommend the Ethereal software.

Offline

 

#3 30-08-2007 10:12:46

rakesh
Member
Registered: 24-08-2007
Posts: 2

Re: P8511 Modbus read issues

Thanks for the reply.
From the screen shot it looks like you have an older version of modbus poll software.
I used the same settings you mentioned with the latest version of mbpoll (4.3.1 Build 272 on WinXP).

The first read after a fresh connect is OK.
Probably because transaction id is zero.

000000-Tx:00 00 00 00 00 06 01 03 9C 40 00 0A
000001-Rx:00 00 00 00 00 17 01 03 14 00 E4 6F 6E 03 E8 FF CE 00 0A 00 1E 27 0F 6F 6E 04 E2 FD DA

The second read onwards mbpoll shows transaction id error. Compare first two bytes in the sequences above and below.

000002-Tx:00 01 00 00 00 06 01 03 9C 40 00 0A
000003-Rx:01 00 00 00 00 17 01 03 14 00 E4 6F 6E 03 E8 FF CE 00 0A 00 1E 27 0F 6F 6E 04 E2 FD DA

Looks like there is a bug in the latest version of mbpoll software or the latest version of mbpoll has exposed a bug in the sensor.
(say if the older verison of mbpoll always used transaction id zero...)
Anyways I can add code to send a modbus request and parse the reply.

Thanks again !.

Offline

 

#4 03-09-2007 14:17:34

PavelM
visitor
Registered: 29-05-2007
Posts: 45

Re: P8511 Modbus read issues

You found a bug in our firmware. We fixed this in our new firmware 4-5-1.02. You can download this firmware from our www pages www.cometsystem.cz.