I had P8541.T3511 and T7511
I set T3511 and T7511 as same as P8541….
But T3511 and T7511 can’t show on www page.
Could you tell how I can do?
Offline
What are the IP addresses of devices? Every device MUST have a unique IP address on your network. Can you set the T7511 and T3511 via our TSensor program?
Offline
Yes, I set the unique IP address for T7511 and T3511
I can see T7511 and T3511 in TSensor program ,but can't show in www page.
I have P8541.
I have set P8541 in TSensor Program and it can show in www page.
I have set T3511 and T7511 as same as P8541….
But T3511 and T7511 can’t show on www page.
Could you tell how I can do?
Offline
IP addresses just in Intrante of my company
Offline
Check if the www is enabled.
If sensors are in other subnet, don't forget to set gate IP and netmask.
Disable firewall ( only for test)
If this doesn't help, what is the error message in your web browser? What is the sensors IP, gate, netmask settings? What is your PC network settings?
Offline
The error message is "http 404-Not Found"
My sensors IP:192.168.0.191 gate:192.168.0.1 netmast:80
It just in Intrante of my company. not connect from outside.
I use the same setting in P8541. P8541 can show in www page.
Why T3511 and T7511 can't show?
Could you tell how I can do?
thanks
Offline
I suppose, your company netmask is 255.255.255.0. Set netmask in sensors to 0. The default sensors www port is 80.
What are the IP's of others sensors? What is your PC IP (ipconfig command)? Please report back.
Offline
Yes,My netmask is 255.255.255.0
I changed setting netmask in sensors to 0,but it also can't show in www page.
The www port is 80, it needs to change or not .
IP:192.168.0.191 use to test T3511 T7511 and P8541,but not at same time.
Microsoft Windows XP [版本 5.1.2600]
(C) Copyright 1985-2001 Microsoft Corp.
C:\Documents and Settings\Edward>ipconfig
Windows IP Configuration
Ethernet adapter 區域連線:
Connection-specific DNS Suffix . :
IP Address. . . . . . . . . . . . : 192.168.0.193
Subnet Mask . . . . . . . . . . . : 255.255.255.0
Default Gateway . . . . . . . . . : 192.168.0.1
C:\Documents and Settings\Edward>
Offline
Don't change the www port.
Set unique IP address for all your sensors. report back.
Offline
I think, the problem is in your proxy server settings. ( It could be long time for ARP cache, or something else...)
You have a few possibilities, how to test the T3511:
1. Set to T3511 by that time unused IP and try to connect again.
2. Enable in your web browser choice "Don't use proxy for local connections"
3. Connect the T3511 directly with crossed cable. Don't forget manual set IP on your computer.
4. Try to delete your ARP table
arp -d
Offline
Could you teach me,how to delete my ARP table .
Step by step
I find one thing that there is a number 3 on my T3511's LCD
That is normal or not
Thanks
Offline
On your computer you can delete ARP table from command line (Start/run/cmd) by these presents command:
arp -d
This command erase ARP table only on your computer, not on servers and others net devices. For more information about ARP protocol please visit http://en.wikipedia.org/wiki/Address_Re … _Protocol, or contact your administrator.
The number 3 on left lower display corner signalizing, that you have closed write-protect jumper in device, you can write calibration constants to your device. The default jumper state is open.
Offline